Does the NEC require any special provisions for self checkout locations? Is there any GFCI requirements for receptacles or grounding requirements for the light poles in these locations?
So the receptacle does not need to be GFCI protected and the light pole only needs to have an equipment ground attached?
As 480parky points out, 210.8 is where you need to look.Its a new install.
The OP is asking about NEC requirements, not specifications.Well it's been a few years for me, so their panel notes could have changed, but it used to be that if a circuit description in the panel schedule was followed by "(5)", the circuit required GFCI, and if it was a "(6)", the circuit required GFEP. If the engineer called out anything above code requirements, that's where I'd think you'd find it. Again though, most of these connections are pretty well detailed in WM's proto drawing sets. If you haven't been provided with any drawings, I'd request them. Even if this is a smaller renovation w/o engineered drawings, I'd imagine the store manager should be able to get you their typical details.
422.5 (5)....does this not come into play ?As 480parky points out, 210.8 is where you need to look.
Roger
Not sure, but I don't think typical self checkout at Wal Mart fits the definition as it appeared in 2014 NEC.As 480parky points out, 210.8 is where you need to look.
Roger
422.5 (5)....does this not come into play ?
Do you know where "Vending Machine" definition was moved to in 2017.
These don't dispense products or merchandise, you bring products/merchandise to them.