Existing client for a 100' x 250' building where I previously issued drawings for a 120/208V service. Client changed it to 460V service and hired an "electrician" to make the changes. Need me to revise my drawings.
My first clue there was a problem was when the electrician said "I've done thousands of jobs like this". To which I replied you have violated the code thousands of times!
75 KVA 480-120/208V dry type transformer. 90A primary breaker. 200A 120/208V panel board with 200A breaker. Transformer was also <6" from wall. Electrician said he could have his engineer provide stamped drawings.
There were other "issues". No way was I going to re-stamp my drawings for this situation. Client, who is a friend, understood my walking away.