I am working on a project that has walk-in coolers and freezers. I?m very confused about the code requirements for protection. The equipment submittals state that the 208V single phase evaporators are powered from the 208V three phase condensing units.
Nameplate for Freezer equipment is:
? Compressor = 11 RLA, 208V 3 phase, (2) Fans = .7A, 208V 1 phase each, MCA = 14.8A, Max fuse = 25A
? Evap nameplate states (3) fans = .45A (1/15hp), 208V 1 phase each, heater = 13A, MCA = 15A, Max circuit protection = 20A
The condensing units have hermetic refrigerant motor compressors so they fall under NEC 440. The evaporator motors do not have these compressors, so do they fall under NEC 430?
NEC 440.8 states a refrigeration system shall be considered to be a single machine and that the motors are permitted to be located remotely from each other, and references exceptions to 430.87 and 430.112 indicating (with conditions) that they can have a single controller and single disconnecting means. Does this mean a 3 phase fused disconnect ahead of the CU is sufficient, even though the evaporator is single phase with MOP = 20A? Or does the evaporator need a disconnect (with OCP) located within sight to satisfy the nameplate requirements?
If so, is a 25A fused disconnect per CU nameplate the proper size? That is the rating for the CU, but the evap has additional motors and a heater? What is the proper method of sizing the disconnect, MOP and circuit conductors for this situation?
The factory states the heater is used for defrost mode, in which case the CU is not running, however, the field technicians say they encounter breaker tripping issues because the CUs take a minute or so to shut down, so for a short while they are simultaneous.
Suppose a situation with slightly different equipment (evaps are still fed from CU). The CU requires max fuse = 25A but the additional loads of the evaporator calculate out to something more, say 40A (perhaps it has a larger heater), how do you size the protection for the single disconnect per 440.8?
Thanks!
Nameplate for Freezer equipment is:
? Compressor = 11 RLA, 208V 3 phase, (2) Fans = .7A, 208V 1 phase each, MCA = 14.8A, Max fuse = 25A
? Evap nameplate states (3) fans = .45A (1/15hp), 208V 1 phase each, heater = 13A, MCA = 15A, Max circuit protection = 20A
The condensing units have hermetic refrigerant motor compressors so they fall under NEC 440. The evaporator motors do not have these compressors, so do they fall under NEC 430?
NEC 440.8 states a refrigeration system shall be considered to be a single machine and that the motors are permitted to be located remotely from each other, and references exceptions to 430.87 and 430.112 indicating (with conditions) that they can have a single controller and single disconnecting means. Does this mean a 3 phase fused disconnect ahead of the CU is sufficient, even though the evaporator is single phase with MOP = 20A? Or does the evaporator need a disconnect (with OCP) located within sight to satisfy the nameplate requirements?
If so, is a 25A fused disconnect per CU nameplate the proper size? That is the rating for the CU, but the evap has additional motors and a heater? What is the proper method of sizing the disconnect, MOP and circuit conductors for this situation?
The factory states the heater is used for defrost mode, in which case the CU is not running, however, the field technicians say they encounter breaker tripping issues because the CUs take a minute or so to shut down, so for a short while they are simultaneous.
Suppose a situation with slightly different equipment (evaps are still fed from CU). The CU requires max fuse = 25A but the additional loads of the evaporator calculate out to something more, say 40A (perhaps it has a larger heater), how do you size the protection for the single disconnect per 440.8?
Thanks!