Did you mean “ I believe this is…”I don't believe this is building code and/or fire code issue. Not electrical.
Yes, that panel work space conflict with door.I will be issuing a violation notice citing 110.26(A) for the location of panel NSP2RP4.
Thanks!Fire rating of walls in not an NEC issue. Please review section 90.1
Yes thank you.Did you mean “ I believe this is…”