I have space wall heater with full load amps of 16.7A. The engineer provided 20A breaker should it not 25A?
424.4 Branch Circuits.
424.4(A) Branch-Circuit Requirements.
An individual branch circuit shall be permitted to supply any volt-ampere or wattage rating of fixed electric space-heating equipment for which the branch circuit is rated. Branch circuits supplying two or more outlets for fixed electric space-heating equipment shall be rated not over 30 amperes. In other than a dwelling unit, fixed infrared heating equipment shall be permitted to be supplied from branch circuits rated not
over 50 amperes.
424.4(B) Branch-Circuit Sizing.
The branch-circuit conductors for fixed electric space-heating equipment and any associated motors shall be sized not smaller than 125 percent of the load.
So from the code sections posted is it code compliant?#12 awg
So from the code sections posted is it code compliant?
The minimum conductor size is 16.7*125%=20.875 amps. #12 for this load is a 20 amp conductor. Is this a 2000 watt heater?
The minimum conductor size is 16.7*125%=20.875 amps. #12 for this load is a 20 amp conductor. Is this a 2000 watt heater?
Unless there is a rule that allows you to truncate the digits after the decimal point the conductors are too small given the 125% requirement.
Certainly, #10 Cu has an ampacity of at least 30A, so it complies with 424.4(B).Would it be okay if conductors are changes to #10 awg but breaker remains 20A?
What do you think?Would it be okay if conductors are changes to #10 awg but breaker remains 20A?
424.4(A) Branch-Circuit Requirements.
An individual branch circuit shall be permitted to supply any volt-ampere or wattage rating of fixed electric space-heating equipment for which the branch circuit is rated
What do you think?
I think that you're on to something. The conductor size would not be reduced to 20 amps under article 240 since that mentions only the OCPD size.Seems to me that if the heater is supplied by a 75C wiring method, and the heater and breaker terminations are rated 75C, then the ampacity of #12 Cu is 25A.