Wall-mounted emergency or exit light terminations

Status
Not open for further replies.

ngd4130

Member
NEC 300.15 - Boxes, Conduit Bodies or Fittings - where required; (E) Integral Enclosure - a wiring device with integral enclosure identified for use. QUESTION: Does a wall mounted emergency light or exit light qualify as this device? Is there another code section which further explains? How are other inspectors treating these applications? Are junction boxes required to be roughed in so the light can be mounted on the box? Thanks.
 

iwire

Moderator
Staff member
Location
Massachusetts
EBUs and Exit signs are nit devices so that section does not apply.

What do the instructions for the EBUs and Exit signs say?

Most likely both require boxes.
 