Wall mounted xfmr

Status
Not open for further replies.
Can anyone help me with the code on mounting a xfmr on a wall above a panel. Code seems to say nothing above the panel if is more than 6" beyond the front of the panel. I was told there is an exception for xfmr's below 50 kva but I can't find it.
 
There is no exception unless it is over 6 feet above the top of the panelboard. 110.26(E)(1)(a)

http://forums.mikeholt.com/showthread.php?t=59425

If I understand his question, he stated the transformer was mounted beyond the front of the panel so it should be o.k, as long as there is the required headroom (as I see it). 450.13 addresses transformers in concealed locations.
As I read it, the "6ft above the top of the panel" only apples to the area above the panel depth.
 
Not sure if this picture came through but it is a picture of the installation in question. Code violation ?

picture didn't show up. Basically I have a xfmr above the panel with ample space behind for conduits and air flow and is above 6 ' from the floor.
 
Last edited:
Not sure if this picture came through but it is a picture of the installation in question. Code violation ?

picture didn't show up. Basically I have a xfmr above the panel with ample space behind for conduits and air flow and is above 6 ' from the floor.

You need 6-1/2 feet working clearance height.
 
From the floor if the top of the panel is 61/2' anything above is ok. Or 61/2 feet from the top of the panel up is off limits.
I am not sure what you are saying, and not sure if you are asking a question. But to be clear, there are two separate requirements. One has to do with the space in front of the panel. You need to keep clear the space that is at least 30" wide, at least 36" deep (more, depending on certain conditions), and 6-1/2 feet high from the floor. This area is reserved for working space for a future maintenance person to use. The other has to do with the areas directly above and below the panel. The area below has to be free of foreign piping or other items all the way to the floor. The area above has to be free of foreign piping or other items for a distance of 6 feet above the top of the panel. These areas are reserved for future installation of conduits.

In the installation under discussion, a transformer would not be "foreign" to the panel. Therefore, it can be placed directly above the panel, and need not be 6 feet higher than the top of the panel. If, however, it sticks out from the wall more than 6 inches further than the panel sticks out from the wall, then the bottom of the transformer cannot impede upon the working space headroom requirement of 6-1/2 feet.

 
I am not sure what you are saying, and not sure if you are asking a question. But to be clear, there are two separate requirements. One has to do with the space in front of the panel. You need to keep clear the space that is at least 30" wide, at least 36" deep (more, depending on certain conditions), and 6-1/2 feet high from the floor. This area is reserved for working space for a future maintenance person to use. The other has to do with the areas directly above and below the panel. The area below has to be free of foreign piping or other items all the way to the floor. The area above has to be free of foreign piping or other items for a distance of 6 feet above the top of the panel. These areas are reserved for future installation of conduits.

In the installation under discussion, a transformer would not be "foreign" to the panel. Therefore, it can be placed directly above the panel, and need not be 6 feet higher than the top of the panel. If, however, it sticks out from the wall more than 6 inches further than the panel sticks out from the wall, then the bottom of the transformer cannot impede upon the working space headroom requirement of 6-1/2 feet.

The last paragraph is exactly what I am looking for. Thank you very much!
 