Today I started to rough wire a new home. The interior decorator wants to install two wall sconces over the tub. The tub is a hydromassage tub, set into a platform. She says she does it all the time. Article 410.4(D) states cord connected,hanging, track lighting and paddle fans, nothing about wall lights. It seems to me that they are allowed. Any comments appreciated.
 

bphgravity

Senior Member
Location
Florida
Re: Wall sconces over tub

This topic has been covered before on this forum, you may want to perform a search for it.

The code does appear to not limit the installation of a surface mounted fixture, be it on a wall or ceiling from being in a bathtub or shower area.

I personaly think there is real hazard potential, and would prefer not to install any type of electrical equipment within the zone specified in 410.4(D).

The homeowner/designer should be made aware of the dangers involved, and GFCI protection should at least be figured into the circuit. :)
 

bennie

Esteemed Member
Re: Wall sconces over tub

Wall sconces are permitted in the tub area, as long as they don't become a grab rail.

Where is the danger? Even changing a lamp while standing in the tub filled with water. We all know about wall switches.
 

pierre

Senior Member
Re: Wall sconces over tub

As a contractor today you really have to protect yourself. People do really stupid things that we cannot prevent. There is a picture of a maintenance man changing a bulb, with his ladder (aluminum) in the pool. JEEZ!!!


Pierre
 

bill addiss

Senior Member
Re: Wall sconces over tub

George,

It would be interesting to hear what the decorator has to say if you asked them to sign something stating it was their design and that you had advised against it.

I agree with Bryan that the Homeowner should be made aware that it's not the best idea, and that a GFCI should be used if the sconces are installed.

Bill
 

bennie

Esteemed Member
Re: Wall sconces over tub

Please tell me what is so dangerous about a light fixture being over a tub?
 

bill addiss

Senior Member
Re: Wall sconces over tub

Bennie,

If you disagree please explain why a light fixture over a Bath Tub cannot be dangerous.

[ July 01, 2003, 03:23 AM: Message edited by: bill addiss ]
 

bennie

Esteemed Member
Re: Wall sconces over tub

I disagree with the fact of being over the tub increases the hazard.

Examine a properly wired fixture...If the enclosure is metal, it will be grounded. If the enclosure is non-conductive, no danger.

The only place in the fixture that is active is the center tab on the lamp holder. To make contact, you would have to remove the lamp and stick your finger in. A person doing that will stop very soon.

A flush light over a tub is dangerous due to the ladder position necessary for relamp.

The tub proximity does not increase the hazard level, in most cases.

To receive a shock, a person has to be inline with a potential voltage, between two conductors.

I have no grounded conductive material in my bath room, to provide the necessary conductor for the other half of the circuit.

Should there be any statistics to prove a wall sconce is dangerous, above a tub, I am sure there would be action by the CPA.
 

bphgravity

Senior Member
Location
Florida
Re: Wall sconces over tub

What bothers me is that the code does appear to consider a bathtub/shower area to be an 'electric free' zone.

240.24(E) - No OCD in dwelling unit bathrooms.

406.8(C) - receptacles shall not within a bathtub or shower space.

410.4(D) - no hanging lights within the zone.

Plus, the code is very restrictive for lighting and other electrical equipment installed near or around pools and like. Article 680.

So, in my opinion, if I can't put my OCD panelboard in the bathroom, and I can't put any receptacles in the tub area, and I can't put any hanging fixtures in the tub area, than I probably shouldn't put any other readily accesible electrical devices or equipment in the area even though the code does not specificaly prohibit this.

I don't mind recessed fixtures with shower trims, and if you can meet the requirements of 410.4(D) when installing sconces or surface mounted fixtures, then I feel you are providing a better service to the customer. :)
 

bennie

Esteemed Member
Re: Wall sconces over tub

When an interior decorator is involved, believe me; the wall sconces will go in.

Hanging fixtures must be out of reach to prevent them from becoming grab rails. Switches, and receptacles, are prohibited, due to requiring physical contact to operate.

Anyone making contact with a wall sconce, while bathing, has a real problem. The height should eliminate any contact by a child.

This is only an imagined hazard.
 

bill addiss

Senior Member
Re: Wall sconces over tub

Bennie,

The average Bathroom does have metallic (therefore grounded) plumbing. I have seen many miswired and ungrounded fixtures.

Can you say that there no difference between touching a live conductor standing on a wooden or carpeted floor and a Bathtub full of water with grounded plumbing fixtures?

My guess would be that there are no statistics on problems because not very many people would ask for this installation in the first place.

Bill

[ July 01, 2003, 11:04 AM: Message edited by: bill addiss ]
 

bennie

Esteemed Member
Re: Wall sconces over tub

Bill: I agree, we all know, incorrectly installed electrical equipment can present a hazard, regardless of the location.

The question is; does the tub and fixture proximity, raise the level of hazard in a properly installed fixture. I maintain that it does not. Statistics of home safety accidents validate my position.
 

bill addiss

Senior Member
Re: Wall sconces over tub

Bennie,

Lack of Statistics, in itself, doesn't prove anything. I feel that if this was a more common installation practice there would be some statistics to see.

I agree that many dangers involving Electricity are due to improper installation and/or lack of common sense in some way. But that's not something you can control. There will always be a number of improper installations and they are more dangerous under some conditions than they are in others. And there is no way to guarantee what small children will do.

Keeping these things in mind I would have to say that the practice of installing wall-mounted light fixtures in Tub and Shower areas is generally not a good idea and if it must be done GFCI protection would make it safer.

Bill
 

bennie

Esteemed Member
Re: Wall sconces over tub

Bill: You are correct and have the proper attitude. I don't see a problem, neither does the NEC. If there is a substantiated problem I'm sure it will be handled.

The new post asking about a panel being installed close to a drinking fountain is another example of "water and electricity paranoia".

A grounded surface to another grounded surface does not present a safety hazard. A fixture canopy or screwshell, to the water pipe, does not have a difference in potential.
 

bill addiss

Senior Member
Re: Wall sconces over tub

Bennie,

I remember you presenting this same situation several years ago and looking for a reason to Red Tag it because you didn't think it was safe. Do you remember that?

Bill
 

canadian

Member
Location
Canada
Re: Wall sconces over tub

Bennie,
Wouldnt a wet body have less resistance and therefore more amperage going through you to ground be a concern?Amperage is what kills.I agree that gfci is minimal in this case and at the same time question why gfci is required in the kitchen.Only your hands would be wet there.They are not used in Canada in kitchens or basements or garages by the CEC....not that this makes it right or wrong.
 

bennie

Esteemed Member
Re: Wall sconces over tub

Canadian: This is apparently a fibre-glass tub. It not easy to stand up inside one of these tubs, while taking a bath.

I can't imagine anyone changing a lamp or touching the fixture while naked and wet :(
 

canadian

Member
Location
Canada
Re: Wall sconces over tub

why is it hard to stand up in a fiberglass tub?? As far as changing lightbulb while naked...not only kinky, just plain stupid.There's a lot of those people around though.
 