walloutlets in office building

Status
Not open for further replies.

easymac

New member
WOULD LIKE TO KNOW HOW MANY DUPLEX RECPTACLES YOU CAN PUT ON A 20 AMP CIRCUIT IN A OFFICE BUILDING ALSO NEED CODE REFFERENCE. THANKS FOR YOUR HELP. EASYMAC
 
Re: walloutlets in office building

220.3(B)(9)

Roger
 
Re: walloutlets in office building

We NEED to know the voltage!!!! And Don needs to know who specified it!

Sorry, read Roger's post and that should tell you.


Roger: Did your ears perk up when you saw this question asked?
 
Re: walloutlets in office building

220.3(B)(9) just gives us a calculated load. We have to combine the calculated load with 210.11 to come up with the maximum number of receptacles permitted on the circuit. And, yes, we do need to know the circuit voltage. See 220.2
Also read this thread.
Don
 