I got a replace a service for Church. The calculated load is under 400 amps it’s 285 I have a 400 320 amp continuous meter. I’m putting in. It goes to two 200 amp disconnects
So I can size my wire just off the 285 since it’s feeding two 200 amp disconnects correct I was thinking running 250 KC Mill parallel aluminum but if they were going to a 400 amp panel, I would have to size it off 400 A correct
250s are a problem only cause I gotta derate.
So I can size my wire just off the 285 since it’s feeding two 200 amp disconnects correct I was thinking running 250 KC Mill parallel aluminum but if they were going to a 400 amp panel, I would have to size it off 400 A correct
250s are a problem only cause I gotta derate.