Wired a single family dwelling with detached garage. I had stubbed into the wall (before slab poured) 1 1/4" PVC schedule 40 to feed the garage panel. Garage panel was to feed simple garage load & water well. The owner added 30 amp 120 volt RV receptacle, 120 volt (probably) circuit for air compressor.
Same well people ran #10/2 w/g UF for well next door, put it on a 60 amp breaker feeding panel at the well, which they put a 2 pole 30 for well, 2 pole 30 for large capacity holding tank with aerator, and 1 pole 20 for duplex receptacle for water softener.
Due to the unexpected added load on the garage panel, I now am thinking of running 90 amp feed to garage panel. This would be with 2 #2 XHHW Al. 1 #4 XHHW Al. and 1 #6 THWN Cu. Conduit has 4 90s in it.
According to my calculations this should be permissible. Not an easy pull, but permissible? :?
Your opinion.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Due to the unexpected added load on the garage panel, I now am thinking of running 90 amp feed to garage panel. This would be with 2 #2 XHHW Al. 1 #4 XHHW Al. and 1 #6 THWN Cu. Conduit has 4 90s in it.
According to my calculations this should be permissible. Not an easy pull, but permissible? :?
Your opinion.
That will not be a hard pull at all. You can buy 2/2/4/6 mobile home feeder instead of individual conductors and it will be even easier because the conductors are twisted together.
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
According to table C.10 you can put 5 #2 XHHW in a 1-1/4" so your configuration which is less conductors and two are smaller will definitely work.
 