Warehouse loading dock leveler & truck restraint conduit install

Status
Not open for further replies.

SamsTLC

Member
Location
Ocean county, NJ
Occupation
Electrical Contractor
Hi all, I am starting a warehouse project with a specified loading dock leveler and truck restraint. I have never wired these and need help figuring out the conduit locations.
When I was bidding on the job I figured out the general concept, namely, Install in the ground before they pour the slab a conduit stubbed up at the wall near the garage doors so I can later install wiring to the exact location.
My question is, what is the location I need to be at for the leveler and truck restraint? Looking online gave me new clues and when I asked the GC he said it was at the standard location (whatever that means).
Any help would be greatly appreciated. I attached a screenshot of the plan specs as well.
Sam
 

Attachments

  • Loading dock.pdf
    76 KB · Views: 24
You need to get the cut sheet (submittal) for the exact dock leveler going in. They will have all of the exact locations that conduit and boxes are needed. You should be able to get that information either from the Architect or the GC. But you need to get it before the slab goes in.
 
You need to get the cut sheet (submittal) for the exact dock leveler going in. They will have all of the exact locations that conduit and boxes are needed. You should be able to get that information either from the Architect or the GC. But you need to get it before the slab goes in.
Thanks! Yup, I got the cut sheets. All the info was on them. Straightforward installation.
 