300.5(D) Protection from Damage. Direct-buried conductors and cables shall be protected from damage in accordancewith 300.5(D)(1) through (D)(4).
(1) Emerging from Grade. Direct-buried conductors and
cables emerging from grade and specified in columns 1 and
4 of Table 300.5 shall be protected by enclosures or race-
ways extending from the minimum cover distance below
grade required by 300.5(A) to a point at least 2.5 m (8 ft)
above finished grade. In no case shall the protection be
required to exceed 450 mm (18 in.) below finished grade.
(2) Conductors Entering Buildings. Conductors entering
a building shall be protected to the point of entrance.
(3) Service Conductors. Underground service conductors
that are not encased in concrete and that are buried 450 mm
(18 in.) or more below grade shall have their location iden-
tified by a warning ribbon that is placed in the trench at
least 300 mm (12 in.) above the underground installation.
(4) Enclosure or Raceway Damage. Where the enclosure
or raceway is subject to physical damage, the conductors shall
be installed in rigid metal conduit, intermediate metal conduit,
RTRC-XW, Schedule 80 PVC conduit, or equivalent.