Wash bay lighting, dry type fixtures protected by an arc fault

Status
Not open for further replies.

Cjfer49

Member
Location
Mn
Occupation
Electrician
An industrial electrician installed dry type fixtures in a wash bay, using MC for branch circuit. He used an Arc fault breaker and explain to all who were in controversy that it was a safe installation. My question is? Can you violate the code and then instal an ark fault breaker? Need some help to kindly persuade him to correct errors.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Can you violate the code and then instal an ark fault breaker?
No you can't. And if that electrician thinks that an AFCI device will prevent a person from receiving a shock when water hits a fixture not rated for damp or wet environments, then they need to go back to school. AFCI devices have one and only one function, and that is not it.

Welcome to the forum.
 

Cjfer49

Member
Location
Mn
Occupation
Electrician
No you can't. And if that electrician thinks that an AFCI device will prevent a person from receiving a shock when water hits a fixture not rated for damp or wet environments, then they need to go back to school. AFCI devices have one and only one function, and that is not it.

Welcome to the forum.
Thank you! Your feedback is very helpful.
 