I have 3.8kw washer at 208v single phase, 18A FLA and 4.16kw dryer at 208V single sing phase at 20A FLA.
Based on above 18x1.25= 22A which is 25A breaker and 20x1.25=25A which is also 25A breaker.
I searched in appliance section NEC 2017 section 422 but not sure which section applies for sizing overcurrent protection of the washer and dryer.
Which NEC 2017 Article section applies for sizing of washer and dryer breaker size? Would 25A be ok or 30A be ok?
Based on above 18x1.25= 22A which is 25A breaker and 20x1.25=25A which is also 25A breaker.
I searched in appliance section NEC 2017 section 422 but not sure which section applies for sizing overcurrent protection of the washer and dryer.
Which NEC 2017 Article section applies for sizing of washer and dryer breaker size? Would 25A be ok or 30A be ok?