Re: washer/dryer combo
This is an oddity, I must admit. I agree that you count 1.5 KVA for the ?required laundry outlet.? I also agree with physis, that you don?t also count an additional 1.2 KVA. Actually, counting an additional 1.2 KVA is not even an available option. If you count a dryer at all, you count it as 5 KVA, or the nameplate rating, whichever is higher, per 220.18.
But the way I see it is that there will be no separate outlet for the dryer. The washer and dryer share a common power connection, and you don?t treat them as separate entities. Therefore, in your service calculation, you don?t list a dryer among the loads.