I just had a bizzare electrical encounter. I went to a trouble call and when I got there the lady told me her Maytag combo washer/dryer decided to stop woking properly After 7 months of faithful service. She had a maytag tech there and he told her that the neutral is dropping out when loaded. The first thing I discovered is that there was no neutral but a 10/2 with ground connected to a 3 prong dryer recep. I read 240v between the ungrounded conductors and 126v on one to ground and 105v on the other to ground. The bonding strap on the terminal block center lug was connected to the frame because of the 10/2 feed as it should be. But I also read 120 volts to ground off the 30A breaker feeding it. Now for the fun part. When I plugged the unit in, I read 3 volts to ground on one leg & 238 volts to ground on the other!! I think it was an open heater coil in the dryer. I told her to contact Maytag. P.S. I checked the ground connection in the panel and it was good. The other thing that comes to mind is someone tapped off the feed where I can't see it. Your thoughts? Jerseyboy