210.12 (B) Does not require 240v outlets to be AFCI, but if it is 120v, it would be on its own circuit, and I think it would fit into the requirements of 210.12 (B). As far as GFCI, 210.18 (7) requires all 120v receptacles within 6 feet of a sink to be protected. If there is no sink it does not need to be GFCI.