Washington State Admin. Exam Inverse time circuit break

Status
Not open for further replies.
Can anyone Help?
What size inverse time circuit Bkr. for this feeder supplying the following motors on a 480 volt three phase delta system?

One 15 hp, two 10 hp, one 75 hp @ 15 minuite intermittent duty.

I have done it this way, am I wrong?
75 hp Full load amps = 96
96 amps x .85 (intermittent duty cycle art-430.22E)x 250% (inverse time Bkr.Art-430.52)
96 x .85 = 81.6 x 2.50 = 204 amps
Then take 204 amps and add the full load currents of all other motors.
204 amps plus
15 hp = 21 amps
10 hp = 14 amps
10 hp = 14 amps
Add these all up and you get 253 amps
with a feeder I cant go up in bkr. size so I have to step down to a 250 amp bkr. (Art-240 overcurrent protection)
Is any of this right? Thanks John
 

traderx

Member
Re: Washington State Admin. Exam Inverse time circuit break

I had this very same question on my test... but the answers were

a:300
b:350
c:400
d:450

But this doesn't match with what you have at 250.

As I would think that this will come up again on my 2nd round ( a variation of it )what would be the correct answer?
 

nicknorth

Senior Member
Re: Washington State Admin. Exam Inverse time circuit break

I need help with this also?? Can anybody show how to do this correctly?? This was also on my WA Admin test.
 

kw

Member
Re: Washington State Admin. Exam Inverse time circuit break

I got this question right on my test, so I'll see if I can help

using your numbers,

the 204 amps is right for the 75hp motor, here is where I think you might have went wrong.

take the 204 x 1.25 since it is the biggest motor to get 255 round this up to the next standard size which would be 300

now add the 21+14+14 to get 349. This is where they try to play games with you. Round down to 300

I believe this would give you the right answer.

Good Luck,

It took me 3 times to pass, just keep with it.
 

nicknorth

Senior Member
Re: Washington State Admin. Exam Inverse time circuit break

Kw do you use table 430.22e for va calc on the service??
 
Re: Washington State Admin. Exam Inverse time circuit break

As I recall, don't you take the highest protection device and then add the flc of the other motors? and then round down. And I have a question without answer about receptacle demand factor on this forum under exam prep and also calculation. Any help?

thanks, Woody
 