From the Washington July Currents (electrical newsletter
Further Delay for 2020 NEC 230.71(B)(4) Requirements - Metering Centers and Power Outlets For metering centers having two to six service disconnects in the same enclosure, we are officially delaying enforcement of NEC 230.71(B)(4) until July 1, 2022. Because of this, the exception to 2017 NEC 408.3(A)(2) supersedes 2020 NEC 230.62(C) until that date. This delay extends one announced in this newsletter in November 2020, allowing metering center manufacturers additional time to make products that do not have more than one service disconnect in an enclosure.When permits are purchased after June 30, 2022, metering center service disconnects must be in separate compartments and comply with NEC 230.71(B)(4) and 2020 NEC 230.62(C).For power outlets certified to UL 231, an indefinite delay applies to enforcement of 2020 NEC 230.71(B)(4) requirements. Because of this, the exception to 2017 NEC 408.3(A)(2) supersedes 2020 NEC 230.62(C). Some of the common uses of power outlets are service equipment for recreational vehicles and temporary power on construction sites.
If NFPA would listen, I would suggest that the appropriate CMPs coordinate changes with UL, especially for GFCI requirements. I suspect that there are some with more connections to me that have conveyed this to NFPA.
Further Delay for 2020 NEC 230.71(B)(4) Requirements - Metering Centers and Power Outlets For metering centers having two to six service disconnects in the same enclosure, we are officially delaying enforcement of NEC 230.71(B)(4) until July 1, 2022. Because of this, the exception to 2017 NEC 408.3(A)(2) supersedes 2020 NEC 230.62(C) until that date. This delay extends one announced in this newsletter in November 2020, allowing metering center manufacturers additional time to make products that do not have more than one service disconnect in an enclosure.When permits are purchased after June 30, 2022, metering center service disconnects must be in separate compartments and comply with NEC 230.71(B)(4) and 2020 NEC 230.62(C).For power outlets certified to UL 231, an indefinite delay applies to enforcement of 2020 NEC 230.71(B)(4) requirements. Because of this, the exception to 2017 NEC 408.3(A)(2) supersedes 2020 NEC 230.62(C). Some of the common uses of power outlets are service equipment for recreational vehicles and temporary power on construction sites.
If NFPA would listen, I would suggest that the appropriate CMPs coordinate changes with UL, especially for GFCI requirements. I suspect that there are some with more connections to me that have conveyed this to NFPA.