Classified locations
Classified locations
It seems many inspectors and contractors steer away from this topic but---
Wastewater pump stations (sewage and storm water) are classified under NFPA 820, and recognized as hazardous under the NEC. Many state and local regulations affirm this requirement. Wiring methods include the use of sealoffs on RMC but most common by exception is an open wiring method for these Class1 Division 1 Group D Locations. There are a couple of other ex-proof methods used in other installations (gas, ..) but for the most part sewage pump manufacturers do not support the installation of ex-proof fittings.
At first look, sealoffs are an easy solution but they are a huge haste when you need to replace the pump. If you want a jbox in the wet well it corrodes and personally - I never liked to have splices in the wet well because of the corrosive environment. I realized years ago in the field contractors tended to install an air gap by stubbing up sch80 PVC conduit from the wet well and leaving "open wiring" to cord grips in the bottom of the jbox/disconnect/panel.
Now my questions -
Has anyone had experience with this method of open wiring, and if so can you reference standards for the air gap or a sketch that emphasizes what the minimum requirements are. I have seen many of these installations, but am not sure what the minimum requirements are.
Also, what limits are placed on this wiring method? Can a screening be placed around the air gap to protect the cables from vandals /rodents and will it still meet the code requirements? I assume this installation would be then similar to a panel pedestal as marketed for the application (and those only have a single small screened vents in solid pedestals from the wet well)...
Thanks in advance.