jmellc
Senior Member
- Location
- Durham, NC
- Occupation
- Facility Maintenance Tech. Licensed Electrician
Went to an office recently for a service call. Lost power to a row of desk receptacles. Briefly looked around desks, saw nothing strange, checked panel and found bad breaker. Soft tripped, still looked on. Wiggled it a little, went to trip position. Then hard to turn off and wouldn't turn back on. OK, bad breaker. Got another, installed it and all good. Went around with tester, all receptacles good. They called back 2 days later it was tripping again. Went back and as I walked by one desk, felt a blast of heat. Looked under and found a space heater on full blast. I am sure it was not there 1st time and I would not think to look for a space heater in mid August, high 90 termperatures. Well, I looked further and found another one 2 desks down. Both women said their legs got cold. I showed them how the 2 heaters together pulled 22 amps. Surprised breaker did not trip sooner. Fortunately, they had another ckt nearby to plug one of them into.
In winter, I always think to look for space heaters but this is the 1st time I'd seen people using them in the peak of summer heat. So, keep your eyes open for anything and always ask what is being used, whether every day or off and on.