I have installed a 125A Service. If I run a Single Conductor, to ground water and Gas pipes , what size is the conductor. I think maybe #3.
 

ryan_618

Senior Member
Re: Water and Gas Pipe Grounding

If you are talking about a grounding electrode system take #8 to the water and #8 to a ground rod. You can not use the gas piping as a grounding electrode. Once you are done with that, bond the gas pipe with a EGC (edit: bonding jumper) sized off of 250.122 (#8? no NEC here). If you have fittings in your water pipe to bond around you can also use table 250.122

[ August 07, 2003, 04:06 PM: Message edited by: ryan_618 ]
 

wmeek

Senior Member
Location
Texas
Occupation
Electrician
Re: Water and Gas Pipe Grounding

This is for bonding of the water and gas pipes.
Code says to run #8 to water, and # 6 to gas. the inspectors says I can combine them and run one wire and loop them. That was what i was wandering on the size of the two would be
 

ryan_618

Senior Member
Re: Water and Gas Pipe Grounding

I really wish I had my code book here, but doesn't 250.104 state that you bond piping systems off of table 250.122??? Also, I thought it said you can use the EGC from the circuit likely to energize the gas piping. I can't think of what that could be other than a furnace that would be on a 20 amp circuit. Have your inspector justify his logic. But ask tactfuly ;)
 

eprice

Senior Member
Location
Utah
Re: Water and Gas Pipe Grounding

250.104(A) referres to table 250.66 for sizing of a bonding jumper to metal water piping. Assuming 1/0 aluminum service entrance conductors for that 125 amp service, #8 copper will suffice. 250.104 (B) referres to table 250.122 for sizing of the bonding jumper to the gas piping, based on "the rating of the circuit that may energize the piping system" :) )

[ August 07, 2003, 05:45 PM: Message edited by: eprice ]
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Water and Gas Pipe Grounding

Keep in mind if you use 8AWG to bond a metal water pipe then it has to be run in conduit if exposed. 250.104 referrs to 250.64(B). Gas piping is considered bonded by the supply circuit, for example an equipment grounding conductor in the supply to a furnace is all that is required.
Also the bonding connection has to be accessible.
 