water cooled transformers

Status
Not open for further replies.

john_g

New member
Does anybody know of standards relating to how water feed and return lines are allowed to used inside electrical panels? Or is it required to have to have the transformers located in there own panels?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
john_g said:
Does anybody know of standards relating to how water feed and return lines are allowed to used inside electrical panels? Or is it required to have to have the transformers located in there own panels?
You may have problems with NEC 110.34(F) & 450.47 if the foreign systems are not integral to the panel or xfmr design.
 