Two questions, #1 Is there an OSHA spec as to how far from an outlet a water cooler must be?, and #2 if so how would you plug in the cooler? An OSHA inspector just told someone there water cooler was too close to an outlet.
Lou
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Ask the OSHA inspector to cite the violation by code, article, and section.

Roger
 

cadpoint

Senior Member
Location
Durham, NC
marissa2 said:
Two questions, #1 Is there an OSHA spec as to how far from an outlet a water cooler must be?, and #2 if so how would you plug in the cooler? An OSHA inspector just told someone there water cooler was too close to an outlet.
Lou
Depends on the spec'd Water fountain. In modest modern installtions the Recp. is under and within the fountain struture itself, thus requiring you
To RFI the information, if not in the Spec. book of the Job.
If its a general hallway recp. that close to fountain tough call
http://www.osha.gov/SLTC/electricalcontractors/index.html
http://www.osha.gov/pls/oshaweb/searchresults.category?p_title=&p_text=devices
Receptacles
http://www.osha.gov/pls/oshaweb/owares.do_search?p_doc_type=STANDARDS&p_search_type=StandTextPolicy&p_search_str=Receptacles

:cool: Chris you just wanted to answer to post your countdown
 

marissa2

Senior Member
Location
Connecticut
Chris
I don't know the full story, I am still getting the information, but it sounds like the cooler is in the hallway and there is a general purpose receptacle
near by. I am still trying to get more on it. Also have a good vacation.
Lou
 

marissa2

Senior Member
Location
Connecticut
I talked to the person that talked to the OSHA inspector, he told me that it was an outlet in the hallway that was too close to the cooler and he wanted that receptacle replaced with a GFCI type. So to keep him happy they repalced it.
Lou
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I agree with Roger,

Have the OSHA inspector cite a code article and section that requires a receptacle near a water cooler to be GFCI protected. The general GFCI requirements for non dwelling units is 210.8(B).

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
raider1 said:
I agree with Roger,

Have the OSHA inspector cite a code article and section that requires a receptacle near a water cooler to be GFCI protected. The general GFCI requirements for non dwelling units is 210.8(B).

Chris


The whole concept is rather silly since even the receptacle feeding the power to the water fountain doesn't require GFCI protection.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
infinity said:
The whole concept is rather silly since even the receptacle feeding the power to the water fountain doesn't require GFCI protection.

Agreed

Just look how many electrical inspectors have ther own ideas.

I have a lot of my own ideas, but if it isn't a code requirement then I don't cite it.

Chris
 