Water filters
celtic
NJ
When putting in a service, care is generally taken to jump out the water meter.
Nowadays, people put in-line water filters after the meter. These filters are generally of the plastic type. Doesn't this sort of negate the point of jumping out the water meter?
This the type filter I am talking about:
Kenmore Whole House Water Filter
If it doesn't negate jumping out the meter, what's the point in jumping out the meter?
Re: Water filters
The reason for jumping out the meter is so the water company personnel don't get hurt when replacing the meter. The reason for connecting within five feet of entrance to the building is because of plastic piping, filters, etc. that would disconnect the grounding electrode. If a filter is installed, you are required to bond the interior metal water piping system. In other words, either jumper the filter or run another bond to the interior water piping system. :D
Re: Water filters
250.53(D) ... (1) Continuity. Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devicesand similar equipment. ...
Re: Water filters
Celtic, I was young and foolish once, and purchased a filter like the one displayed above. I thought it stood a snowball's chance against my well water (which was hard as a brick and had more iron than a modern car). :)
If a filter were installed anywhere on the system, 250.104 would require a jumper to bond the suddenly disconnected portion of the metallic water pipe system. ;)
Re: Water filters
This is interesting to me. I had a lot of trouble with rocks in my water. I replaced 3 or 4 flush valves on the toilet and had to have a plumber replace the insert on my tub valve twice (almost $100 a pop). The rocks also clogged up my solenoid valve on the washing machine.
I finally paid a plumber to come out and put in one of these filters in front of the water meter. I don't recall seeing a bond wire around it.
Re: Water filters
Do you have copper plumbing? :D
I think the one I purchased was a GE Smartwater, but as I recall neither the water nor I came away smarter from the experience. ;)
Re: Water filters
A piece of #6, two water bond clamps, and you're in business, Bob. Take you five minutes. ;)
I will have to take a look tonight. I never really looked that closely, but I think I would have noticed something that obvious if it was there.
I did notice this odd bond wire around the water meter though. It is no more than a #18. I have often wondered what its purpose is.
Re: Water filters
A piece of #6...
Shouldn't this depend on the service size, unless only a supplemental ground is dependent on this continuity?
Re: Water filters
Larry, by 250.104(A)(1) you're right. The bonding jumper should be sized according to the service, which is silly. But hey, who are we to question? :)
By the way, I have a proposal to change this. :D
Come on George, you really expect us to believe that :D