'17 Code.
I have a building with a 1200 amp service with (3) 600 kcmil Cu.
Metal-Structural Frame building but hold down bolts were not boded to UFER
A #4 Cu was installed to the UFER at time of construction and is connected to the neutral in my service panel.
The steel is bonded with with a 250 kcmil cu per 250.104
I have a metallic underground water line on end of the building opposite the service gear.
250.68 notes building steel can be used to interconnect electrodes but my only electrode is my UFER with the #4 Cu.
My water line requires a 3/0.
Since I have the 250 kcmil boding jumper to the steel from the service can I connect my 3/0 from the water to the steel ?