Date: Wed Aug 20 2003
Report #: 2582
Code: NEC
Section: 424.19(A)(2)(2)
Question:
Is it the intent of this section that it apply to SFR air handlers containing heat strips? Or would 440.14
apply?
Answer:
If the fixed electric space heating equipment incorporates a hermetic refrigerant motor-compressor it must
also comply with Art. 440 (see Art. 424.2). If the air handler has a compressor in it, the disconnecting
means must comply with Article 440.14 and be within sight and readily accessible.
Commentary:
If the fixed electric space heating equipment doesn't contain a refrigerant compressor, the disconnecting
means may be capable of being locked in the open position if not within sight, as allowed in Art. 424.19.