I came across what I think is an obselete installation of a GE plug in breaker for separate metering for an electric water heater. How can I safely remove the source wiring for the water heater without interrupting the current service, if the wiring runs through the current meter can, then through an offset to the out of service meter for the water heater? Has anyone encountered these types of breakers before?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Usually, this dual meter-base setup remains as it is until a service upgrade brings a new meter into the mix. That's when the second cable is deleted, and the water heater supplied from the same panel as everything else.
 

iwire

Moderator
Staff member
Location
Massachusetts
LarryFine said:
Usually, this dual meter-base setup remains as it is until a service upgrade brings a new meter into the mix.

That is how it is handled here as well, or was, it's been a long time since I ran into a dual meter set up. :smile:
 

KJay

Member
Location
MA
It?s not necessarily obsolete, unless of course, your power company doesn?t offer the off-peak rate anymore. :smile:
There are still a few of those dual meter, off-peak setups around my area. Every now and then, I will get a no hot water call and it turns out that the clock in the off-peak meter just needs to be reset because of a power outage of some sort. I?m not sure if our power company even offers an off-peak rate for residential electric water heating anymore, but sometimes customers have me disconnect it just to avoid having to deal with the no hot water situation again.

When I need to disconnect them and can?t wait for the power company to get there to unlock the meter ring, I will advance the time set knob on off-peak meter to one of the off positions to make things at least a little safer, then carefully disconnect and cap off the wires to the DP feed-thru switch in the panel one at a time. I?ll put a standard DP breaker in place of the feed-thru switch to power the water heater.
You just have to remember that the off-peak meter?s switch is only a single line break, so you will still have 120V to ground on one leg, usually fused only at the utility transformer, when you are disconnecting the wires on the line side of the feed-thru switch in the panel.
The power company can then be notified to come and remove the off-peak meter and install a plastic meter blank at their convenience.
 

abe72487

Member
Location
Lewiston Idaho
H W Tank

H W Tank

Our utility use to have a separate line just for the HW TAnk that bypassed the meter and they billed the consumer a flat rate for the HW Tank. This was done in the fifties to get people use to using electricity. These usually were installed by utility lineman and there are still several out there.
 