water heater connection

Status
Not open for further replies.

fishingmaniac

Member
Location
Hull, Mass
If adding a 220v water heater in the typical unfinished basement utility area for a single family residential occupancy with a two pole 30a with romex 10/2 with gnd run from panel to heater,

is it a violation to run that romex directly into the water heater, or must you use a box and change over to greenfield, or is it up to the inspector?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The NEC doesn't care how you wire the water heater unless the wiring method is subject to physical damage which is a judgement call for the AHJ. Maybe someone from Mass will have a more concise answer.

Welcome to the Forum. :)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It's always up to the inspector :D
In our area we do not allow the NM to extend from the ceiling/wall all the way to the water heater as we do not consider that following the surface of the building and at times it may be subject to damage. Commonly the NM is sleeved in some type of flex.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If the panel is not within sight then you need a disconnect at the heater. We use a typical non-fused a/c pullout then we use carflex into the heater. I agree with the others- it is an authority having jurisdiction call but imo the flex makes for a neater job and then there is no issue with protection.
 