what is the correct way i would figure ocpd on a water heater with a 3000w and a 6000w on a 240v circuit
Are you sure it isn't "3000w upper, 3000w lower, 3000w total"?what is the correct way i would figure ocpd on a water heater with a 3000w and a 6000w on a 240v circuit
what i am trying to figure out is would i use the ampacity of both (3000W and 6000W) heating elements or just the bigger of the two im really confused
In the case of theoretical example given, it would depend on the internal wiring of the water heater.
If the elements can never be energised at the same time, then consider only the larger one.
If both elements can be energised at the same time, then consider the total load of both.
In a real world case, the manufacturers instructions should be followed, in addition to the NEC.