rlqdot
- St. Louis, MO - USA
- Professional Engineer (multiple states) - building design
I am designing a project with a 45Kw 120 gallon tank-type water heater operating at 208 V - 3 P. Article 422.13 says I have to consider it a continuous load. The FLA is 125 amps, and 125% of FLA is 156.25, so I believe I need a 175 amp circuit breaker (next standard size above 156.25 amps), with 2/0 THHN copper conductors for the branch circuit.
However, when I refer to article 422.11(F)(3), it seems to limit me to nothing larger than 150 amps for overcurrent protection on water heater branch circuits.