rlqdot
Member
- Location
- St. Louis, MO - USA
- Occupation
- Professional Engineer (multiple states) - building design
I am designing a project with a 45Kw 120 gallon tank-type water heater operating at 208 V - 3 P. Article 422.13 says I have to consider it a continuous load. The FLA is 125 amps, and 125% of FLA is 156.25, so I believe I need a 175 amp circuit breaker (next standard size above 156.25 amps), with 2/0 THHN copper conductors for the branch circuit.
However, when I refer to article 422.11(F)(3), it seems to limit me to nothing larger than 150 amps for overcurrent protection on water heater branch circuits.
Can anyone clarify for me what the correct limitations are on this circuit?
However, when I refer to article 422.11(F)(3), it seems to limit me to nothing larger than 150 amps for overcurrent protection on water heater branch circuits.
Can anyone clarify for me what the correct limitations are on this circuit?