Greetings all I am interested how you all answer this question:
A standard residential 50 gallon water heater has two 4500 watt elements that operate non-simultaneously.
The markings on the water heater indicate 240 Volt, 4500W, copper conductors only.
The manufacturers literature that comes with the water heater has a table for recommended sizing the breaker and wire.
The table lists 10 Awg copper and a 25 amp breaker for this unit.
The breakers are marked for 60/75 C terminations.
If the wiring method chosen will be type MC cable what is the minimum branch circuit conductor size permitted by the NEC?
A) 10 AWG
B) 12 AWG
C) 8 AWG
A standard residential 50 gallon water heater has two 4500 watt elements that operate non-simultaneously.
The markings on the water heater indicate 240 Volt, 4500W, copper conductors only.
The manufacturers literature that comes with the water heater has a table for recommended sizing the breaker and wire.
The table lists 10 Awg copper and a 25 amp breaker for this unit.
The breakers are marked for 60/75 C terminations.
If the wiring method chosen will be type MC cable what is the minimum branch circuit conductor size permitted by the NEC?
A) 10 AWG
B) 12 AWG
C) 8 AWG
(A) is correct 10 AWG , the water heater is a continuous load per 422.13 and since 240.4(D)(5) limits 12 AWG MC to 20 amps and table 240.4(G) only references 'motor operated' appliances not all appliances.