Water heaters and troubleshooting them. I thought this little bit of information might help
someone down the road.
I have been in the Electrical trade for around 40 years, Yes I am old! And most of
this time has been troubleshooting.
Have you never been called to check a water heater and the problem is the overload
cutout is popping out on the upper thermostat? Well this is a common problem and is
usually caused from a thermostat stuck in the closed position the heating elements is
shorted to the case of the heater and the thermostat can?t cut it off ,or thick sludge has
coated around the upper thermostat.
Once I fixed one with this problem and I seen the customer a few months later and
they told me they had to replace the heater because they had another electrician to work
on it and it still did the same thing.I didn?t ask them why they didn?t called me back. I
was afraid of the answer. ?The other electrician replaced the thermostat too.?
But anyway I was called the other day for the same thing the overload was popping
out on a customers water heater.
Checked the heater elements around 13.5 ohms between the terminals on both.
Checked the elements to ground with a high resistance ohm meter to ground they
where both clear.
Checked thermostats with a ohm meter and turned the set screws back and forth to
make sure they where switching on and off right, they checked good.
And as I was getting ready to tell the customer all the electrical checks out and there
must be sludge around the upper element it donned on me that there was something
funny when I turned the upper thermostat up and down .And what it was , the element
was becoming energized when I turned the set screw counterclock wise.
Not really thinking about it all I was interested in was that the stat was switching back and
forth between the two terminal screws.
The person that had put the thermostat in had put the upper thermostat wire where the
lower thermostat wire should be and the lower wire where the upper should be.
And if you examine this circuit with the elements reversed the electrical power is never
shut off to the upper element. So the cutout has no choice it will pop out if working
properly.
Then it donned on me this was probably what was wrong with the heater I mentioned
above.It is easy not to pick up on this so check for this.
Everyone have a Merry Christmas and a great New Year.
someone down the road.
I have been in the Electrical trade for around 40 years, Yes I am old! And most of
this time has been troubleshooting.
Have you never been called to check a water heater and the problem is the overload
cutout is popping out on the upper thermostat? Well this is a common problem and is
usually caused from a thermostat stuck in the closed position the heating elements is
shorted to the case of the heater and the thermostat can?t cut it off ,or thick sludge has
coated around the upper thermostat.
Once I fixed one with this problem and I seen the customer a few months later and
they told me they had to replace the heater because they had another electrician to work
on it and it still did the same thing.I didn?t ask them why they didn?t called me back. I
was afraid of the answer. ?The other electrician replaced the thermostat too.?
But anyway I was called the other day for the same thing the overload was popping
out on a customers water heater.
Checked the heater elements around 13.5 ohms between the terminals on both.
Checked the elements to ground with a high resistance ohm meter to ground they
where both clear.
Checked thermostats with a ohm meter and turned the set screws back and forth to
make sure they where switching on and off right, they checked good.
And as I was getting ready to tell the customer all the electrical checks out and there
must be sludge around the upper element it donned on me that there was something
funny when I turned the upper thermostat up and down .And what it was , the element
was becoming energized when I turned the set screw counterclock wise.
Not really thinking about it all I was interested in was that the stat was switching back and
forth between the two terminal screws.
The person that had put the thermostat in had put the upper thermostat wire where the
lower thermostat wire should be and the lower wire where the upper should be.
And if you examine this circuit with the elements reversed the electrical power is never
shut off to the upper element. So the cutout has no choice it will pop out if working
properly.
Then it donned on me this was probably what was wrong with the heater I mentioned
above.It is easy not to pick up on this so check for this.
Everyone have a Merry Christmas and a great New Year.