I'm a little confused with the proper feeder and over current device for an electric water heater. Referring to 2014 NEC (used in my state now) article 422.11(E)(3) states that nonmotor appliance rated over 13.3 amps overcurrent not exceeding 150 % can be used (then you go to next size up rule if it doesn't match standard OVD). But in 422.13 it says that storage type water heaters 120 gal or less are considered a continuous load (which then would require 125% calculation).
Mike Holts book "Understanding the NEC Volume 1 article 90 - 480" in both of the sections listed shows water heaters and both calculations (150% and 125%).
So I am confused, what is the intent, difference of these two sections and the proper calculation for the OCD (and thus feeder) for electric water heaters for the normal dwelling (keeping in mind the standard 4500 watt or the newer 5500 watt units)
5500 Watt/240 V = 22.9 amps (23) X 150% = 34.5 Amp (OCD 35 amp breaker with # 8 wire) based on 422.11(E)(3)
or
5500 Watt/240 V = amps (23) x 125% = 28.75 amps (30 amp breaker with # 10 wire) based on 422.13
Thanks,
K947
Mike Holts book "Understanding the NEC Volume 1 article 90 - 480" in both of the sections listed shows water heaters and both calculations (150% and 125%).
So I am confused, what is the intent, difference of these two sections and the proper calculation for the OCD (and thus feeder) for electric water heaters for the normal dwelling (keeping in mind the standard 4500 watt or the newer 5500 watt units)
5500 Watt/240 V = 22.9 amps (23) X 150% = 34.5 Amp (OCD 35 amp breaker with # 8 wire) based on 422.11(E)(3)
or
5500 Watt/240 V = amps (23) x 125% = 28.75 amps (30 amp breaker with # 10 wire) based on 422.13
Thanks,
K947