This Rheem water heater has no listing for size of an OCPD nor branch circuit wiring
Without reviewing checking the NEC code book, I believe it’s no more than a 20 ampere breaker for such a water heater 120 gallons or less using 13.33 amperes or less or
150% of rating (current calculated?) if the same conditions but with over 13.33 amperes rating?
I also don’t get why the name plate for 240 volt 1 phase which we’ll be supplying this with is rated 4500 watts for the top heating element and 4500 watts for the second bottom heating element, with total watts listed at 4500 watts. 4500 + 4500?
So if I take 4,500 watts / 240 volts = 18.75 i amperes
Then 18.75 x 1.50% = 28.125 i
Conductor size
= #10 AWG THHN @ 75 degree termination
OCPD
= 28.125 i, next standard size 30 i breaker
Does this sound correct?