6 618electrician Member Location St. Louis Occupation Maintenance electrician Friday at 4:20 PM #1 If the water heater is not visible from the 30 amp breaker in the main panel in basement do i need a disconnect ????????????????????????????????????????????????
If the water heater is not visible from the 30 amp breaker in the main panel in basement do i need a disconnect ????????????????????????????????????????????????
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Friday at 4:24 PM #2 Yes or a permanent locking means on the circuit breaker.