This may be elementary, but 422.13 states that a water heater is to be considered a continuous load. When sizing a feeder, the water heater should be considered as a fixed appliance. If there are 4 or more fixed appliances, then I can apply a 75% demand factor to the appliances (220.53). In all of the literature that I have explored on feeder sizing, I see the 125% factor missing from the water heater in computing the demand load on the feeder. For example, assume I have a 1200VA dishwasher, a 5000VA water heater, a 1000VA disposal, and 1000VA microwave for my fixed appliances. The demand is typically computed as:
(1200+5000+1000+1000)VA x 0.75 = 6150VA
But, what about the water heater being a continuous load???? Why not perform the following computation:
(1200+5000x1.25+1000+1000)VA x 0.75 = 7088VA
Does anyone have the correct answer? Need help.
(1200+5000+1000+1000)VA x 0.75 = 6150VA
But, what about the water heater being a continuous load???? Why not perform the following computation:
(1200+5000x1.25+1000+1000)VA x 0.75 = 7088VA
Does anyone have the correct answer? Need help.