Have a interesting problem. Went on a residential service call for hot tub C.B. tripping(2p 60a GFI)This only happens when there is a heavy rain. Removed wires from breaker left installed in panel, still would not reset. Removed C.B. now it stayed in the on position. Owner says C.B. was replaced two months ago by another electrician who wired the hot tub six months ago. I tapped the C.B. in my hand, I noticed water drops were coming out of the reset button area. I got a hair dryer and dryed the circuit breaker, the breaker reset and the hot tub is now working, test button also works on the breaker. Service is seu cable(no drip loop) meter can is rotted on bottom. Changed riser to pvc, new meter can, left seu cable feed to panel from load of meter. Owner called back few days ago said breaker was tripping again,(after heavy rain) went there & found same condition water in the breaker. The breaker is located in the uppper right position (2&4) right below the main breaker. The seu penetration into the house is caulked, & there is no evidence of water coming into the panel from within the seu cable(Originally I thought this might be the case). Told owner I would have to be here during Rain condition to see Actually what is happening. Just wondering if anybody else had similiar type situation.