Water meter jumper
slc410
Madison wi
Is there any usefulness to jumping the water meter when the water main entering through the slab is plastic pipe then after the water meter pex tubing is ran throughout the house?
Let's be clear that there is no reason to even bond the meter at all in this case.
ONLY if a clueless AHJ inspector insists on it.
Easier to satisfy ignorance with compliance vs. argument or attempt at education.
Happily, worst I've come across is requiring TR receptacles in a woodworking shop !
If the water main is plastic then the metal portion of the water piping system does not even need to be bonded near the water meter.
Just curious- has anyone been required to put a bond across a water meter from plastic pipe to plastic pipe? I mean, to put the clamps on the plastic, just to satisfy an inspector? It would be the height of stupid, but sometimes it's easier to blow a few dollars than to argue.
That's the long and short of it :happyyes:
That is why I was wondering if there was copper on the load side of the meter and the op wanted to know if he had to jump across the meter. Our meters are in the ground outside the homes so it is not an issue but I could see someone enforce jumping across the meter if the connection is on the meter itself when there is plastic outside and copper inside or the reverse. Seems odd but
250.53(D) Metal UndergroundWater Pipe. If used as a grounding
electrode, metal underground water pipe shall meet the
requirements of 250.53(D)(1) and (D)(2).
(1) Continuity. Continuity of the grounding path or the
bonding connection to interior piping shall not rely on water
meters or filtering devices and similar equipment.
I know there are some States that may not enforce this but we've been doing that here in NJ for many years. We also bond across water heaters for the same reasons although I don't know that it specifically states that in a Code section. Also, I live in a lake community and many of the meters along the lake are in the street. We are required to bond any copper piping that enters the house within 5' of where it enters.
Getting back to the OP, I don't see a reason to bond water lines if they are run in PEX yet I'm sure some EI's will make you do that anyway. What I would do in a case like that is run the ground wire to the water meter and leave a whip at that location. There's nothing to attach or bond to. He can't make you bond to PEX.
Why would you run the grounding electrode conductor to the meter if there is plastic coming in. I seriously doubt they will ever go back to a metal piping
I am sure you are correct. However if the E I insisted on it I would just run it there just keep the job moving. I know it is a waste .
The 5' rule is only if the water pipe is being used as an electrode. If you're just bonding the interior metal piping system {250.104} the connection can be at any accessible point along the piping system.
I agree. Would you also say that irrespective of whether the pipe is being used as an electrode or not that the bonding point should be before any fittings, hose bib tap offs, etc. ? Not sure if that's a requirement or not.
Was it a woodworking shop for 4 or 5 year old children?:D
Sorry but my concern wouldn't be how much it is going to cost me to fight the inspector but rather how much this inspector's incompetence may be endangering those he is inspecting for. I think I can find a lot more people that would side with me then would side with the inspector on this issue.
If the inspector is asking for something that doesn't do any harm and the parts and labor cost less than another trip for re-inspection, then I won't start a fight. If the inspector is asking for something that undeniably makes things less safe then yes he'll get an earful from me.
Inspector is also showing his ignorance and you have to wonder what else he is ignorant about. You are doing a community service by calling him out on such issues, if he isn't a poop head he will learn from it and become a better inspector.
Oh, trust me, I'd always call him out. I just won't start a big fight that causes me a failed inspection and a bad relationship that affects future jobs.
A lot of times I find that the inspector won't budge on the job you first call them out on, because they have to save face. But then they mysteriously don't enforce that 'rule' on later jobs.
I likely wouldn't either - depending on what the issue was. This one is bad enough I won't give up too easily. Everyone has a different place to draw that line.