L lholton57 New member Location Richfield, Minnesota, USA Apr 22, 2018 #1 What size should the EGC be to the water meter for a 200 amp residential service fed with #2/0 conductors. Using #4 GEC to ground rods.
What size should the EGC be to the water meter for a 200 amp residential service fed with #2/0 conductors. Using #4 GEC to ground rods.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 22, 2018 #2 #4
Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician Apr 22, 2018 #3 lholton57 said: What size should the EGC be to the water meter for a 200 amp residential service fed with #2/0 conductors. Using #4 GEC to ground rods. Click to expand... I think you mean GEC Welcome to the Forum!
lholton57 said: What size should the EGC be to the water meter for a 200 amp residential service fed with #2/0 conductors. Using #4 GEC to ground rods. Click to expand... I think you mean GEC Welcome to the Forum!
N nickelec Senior Member Location US Apr 22, 2018 #4 And GEC to rods needs to be no larger then #6 Sent from my SM-G950U using Tapatalk