Re: Water Pipe Bond
Hi George,
The water pipe "bond" in this case is distinctly different than 250.52(A)(1) where the water pipe is used as a "grounding electrode".
In this case, the "separatley derived system" (a transformer, for instance), used in an industrial or commercial application will not always be located close to the grounding electrode system for the premises and therefore is required to be "bonded" to the water system in the area in which it serves. Keep in mind, this is a "bond", not a "ground". Also, the exception following helps to understand the intent.
Much different than a house!