It depends where the meter is installed. Locally water meter is installed by the side walk at least 25 away. So if I connect to the water pipe with 5' of entry then I have at least 10' of water pipe contact with the earth before it gets to the meter and I don't have to worry about jumping around the water meter.
However, if the water meter is installed near the dwelling unit then I would say connect on the supply side (before the meter) first then jump over the meter to bond the other side of the meter. Or connect to the customer side first then jump over the meter to the utility side inorder to satisfy the "10' in contact with the soil" rule.