water pipe inside electrical room

Status
Not open for further replies.

480sparky

Senior Member
Location
Iowegia
See 110.26(F)(1)

(1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (F)(1)(d).
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
(b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
(c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.
(d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling..
 
Last edited:

electricalperson

Senior Member
Location
massachusetts
im most electrical rooms i work in, its basically the ultility room. the sprinkler riser enters the building and the water main is close by. just as long as it is out of the workspace and not above the panel its fine