water pipe located behind panel

malachi constant

Senior Member
Location
Minneapolis
Hi all,

This sounds like a straightforward "not a code violation" but figured I would ask the group anyway. Project scope includes replacing recessed panels with new (recessed) panels with more breakers, so the panel openings are being cut a little taller. For one of the recessed panels when the contractor removed it they found a water pipe directly behind the panel, mounted tight against it (or very close to it at least). They suspect it is a rain leader (or whatever they are called) from a roof drain. The new panel is a little deeper than the existing, so the new panel will have to protrude into the space a little bit. If this is a corridor I assume there are ADA concerns about items protruding into a space that will need to be addressed, but I cannot think of anything prohibiting a water pipe (or rain leader) being "tight" against the back of a panel.

My thoughts are to ask if a visual inspection of the existing panel and rain leader show any signs of water damage. If so they should consider relocating the panel (or rain leader), and if they don't want to relocate it they should make the inspector aware of the situation and give them a chance for input. If no water damage is evident then I would allow the panel to remain where located but recommend a water barrier of some kind be installed to protect against future leaks.

Sounds like the panel is recessed in a burnished block wall - meaning it's a nicer finish that will look obviously bad if they have to relocate.

Does my approach sound reasonable? Any other advice?
 

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
The water pipe does not sound like a code violation as far as the electrical code is concerned. If it is a roof drain there should be no standing water in it. I would find out what the pipe is for sure before making a decision. Maybe some insulation between the pipe and the panel would be a good idea
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
"so the new panel will have to protrude into the space a little bit."

Unfortunately 110.26(E) does not address "a little bit"... If the pipe is over the panel, it's a violation.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
"so the new panel will have to protrude into the space a little bit."
The OP was referring to the panel protruding into the room a little farther, as the back of the new, slightly deeper panel will still be up against the pipe.

Cheers, Wayne
 