Water pipe is an electrode-- now it needs a supplemental electrode- my choice rods. Now the question is 1 or 2 ground rods? Assume 25 ohms is not reachable.
One rod is not an electrode if it's not 25 ohms or less.
That doesn't make sense-- 2 rods would not be 25 ohms around here so why would that be an electrode.
250.53 Grounding Electrode System Installation.
***
(D) Metal Underground Water Pipe. If used as a grounding
electrode, metal underground water pipe shall meet the
requirements of 250.53(D)(1) and (D)(2).
***
(2) Supplemental Electrode Required. A metal underground
water pipe shall be supplemented by an additional electrode of
a type specified in 250.52(A)(2) through (A)(8). If the supplemental
electrode is of the rod, pipe, or plate type, it shall
comply with 250.53(A).
250.53 Grounding Electrode System Installation.
(A) Rod, Pipe, and Plate Electrodes. Rod, pipe, and plate
electrodes shall meet the requirements of 250.53(A)(1)
through (A)(3).
(1) Below Permanent Moisture Level. If practicable, rod,
pipe, and plate electrodes shall be embedded below permanent
moisture level. Rod, pipe, and plate electrodes shall be free
from nonconductive coatings such as paint or enamel.
(2) Supplemental Electrode Required. A single rod, pipe, or
plate electrode shall be supplemented by an additional electrode
of a type specified in 250.52(A)(2) through (A)(8). The
supplemental electrode shall be permitted to be bonded to one
of the following:
I have always used 2 rods but then I read the NC interpretation and they are saying only one is required. I started this thread to make sure I had always interpreted it correctly. I still don't get the fact that a single rod isn't an electrode. It is an electrode just not a good one
I agree with Rob, one rod is not an electrode on its own unless it meets the 25 or less requirement.So where does it say a single rod is not an electrode. In 250.52 it states electrodes and a rod or pipe is an electrode... it does not say 2 must be used to be an electrode. I get that 250.53 states you need 2 but does that doesn't mean one is not an electrode....What am I missing.
That doesn't make sense-- 2 rods would not be 25 ohms around here so why would that be an electrode.
I do agree with the need for 2 rods but somehow I was looking for the exact wording that said one rod is not an electrode. It states that but indirectly. We have always added 2 rods when a water pipe electrode was also existing because if the water pipe got changed to plastic then the two rods would be the main electrode.
I agree that the wording is somewhat poor because they're calling the single rod an electrode even though it may not meet all of the conditions of being an electrode. If I have two rods pounded only 7' into the ground that's not an electrode either.
But it does. The definition of "grounding electrode" in article 100 only requires it to be a conducting object that provides a direct connection to planet Earth.. . . they're calling the single rod an electrode even though it may not meet all of the conditions of being an electrode.
Because the number 25 is essentially arbitrary, and because some locations can never achieve that number regardless of the number of rods installed. They had to draw a line somewhere, and "two and done" is where they drew that line.And why you don't need to continue driving rods until it is 25 Ohms or less.
But it does. The definition of "grounding electrode" in article 100 only requires it to be a conducting object that provides a direct connection to planet Earth.
As I said earlier, the question is not whether any particular conducting object can be called a "grounding electrode." The question is whether any such object can, by itself, comprise a complete and compliant grounding electrode system.
Suppose one rod tests at 80 Ohms. Then you drive an identical rod at the requisite minimum 6 ft away. I cannot fathom how the combination of the two rods in parallel in this condition is anything less than 40 Ohms. Is there something going on in the physics of ground rods, that makes the conductance of two rods better than the sum of their individual conductances?
What am I missing, about how "two rods and done" excuses you from any ohm requirements? And why you don't need to continue driving rods until it is 25 Ohms or less.