water pipes in electric room

Status
Not open for further replies.

sam34

Member
Location
Missouri
Can we have a water or A drain system over an electric room. In another word, can we use a pan under the drain or water line? Thank you for your input
 

bphgravity

Senior Member
Location
Florida
Re: water pipes in electric room

Review section 110.26(F)(1) of the NEC to determine compliance. More details of the exact installation will be needed to give a positive yes or no answer.
 

celtic

Senior Member
Location
NJ
Re: water pipes in electric room

I do not neccessarily agre with the whole "pan under " deal...but I have seen it done (and was verbally objective), but was shot down because of 110.26....imagine an expansion joint running diagonally across a switch gear room(480V) protected by a drip pan ...the pan was over most, but not all of the gear - which had 4160 feeding the xmer(in that same room). Virtually EVERY panel on this job had a drip pan over it - pretty sh*tty, but code compliant.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: water pipes in electric room

If the pan and water line are not at least 6' above the top of the equipment, it is a violation.

Steve
 

sam34

Member
Location
Missouri
Re: water pipes in electric room

thank you all for the reply, after reading sec. 110.26(F) it seems a violation to do that. How about running an air ducts over the telephone board, would that be a violation since it's a low voltage system?
 

wirenut1980

Senior Member
Location
Plainfield, IN
Re: water pipes in electric room

thank you all for the reply, after reading sec. 110.26(F) it seems a violation to do that. How about running an air ducts over the telephone board, would that be a violation since it's a low voltage system?
Is your telephone board enclosure waterproof? Just because an installation is code compliant does not mean it won't be a POS. :p
 

ryan_618

Senior Member
Re: water pipes in electric room

Originally posted by sam34:
thank you all for the reply, after reading sec. 110.26(F) it seems a violation to do that. How about running an air ducts over the telephone board, would that be a violation since it's a low voltage system?
Article 800 does not reference 110.26, and therefore it is not a requirement, as per 90.3.
 