All i have a job i just started on with a hvac contractor who is replacing all existing equipment and doing a total repipe. My job is pretty simple just disconnect and reconnect what’s there. Last night we started on a floor that has roughly 50 water source heat pumps. I have drawings from the original build back in 1997. These drawings show two water source heat pumps on one circuit with a 15 amp two pole toggle switch as a disconnecting means. But for the overcurrent protection, they have a two pole 30. Now as I’ve been disconnecting these switches I’ve been finding that they’re 20 amp which is totally fine. But what’s concerning me is that they are on a 30 amp circuit and it’s not being fused down to 15 A as the manufacture nameplate states MOCP 15. I’m just asking for advice on what you guys would do in this situation as I’m only supposed to be disconnecting and reconnecting and I don’t think there is enough money in the job nor does the contractor want us to start Redoing a lot of work. I’ve caught a couple things recently on this job as far as changing out motor starters with VFD‘s and upsizing breakers for the input current. But this is a pretty big situation as there is three floors and there’s about 50 water source heat pumps per floor. Any advice helps.