TX for the responses
TX for the responses
acrwc10 said:
Can you give us some more detail to how this is run , under ground, across a roof, threw a septic tank, etc.?
For under ground conduit coming up in to a panel or building , Duct seal. If a pipe is running under ground down hill , concrete pull box with drain rock at the bottom of the hill.
This is an installation where two (2) 480V, 4000 amp concrete ductbank feeders are brought in from separate 3000 kVA transformers to separate 480V, 4000A switchgear which is located in a building next to the xfmrs.
I haven't actually seen the installation yet, or at least paid attention to the pipe elevations, but I'm afraid the outside pipes are at an elevation that backs up the conduit with water after a heavy rain. There's containment for the liquid-filled padmounts that fills up after heavy rains, and is slow to drain down. It's the flow-through membrane type that plugs if it senses oil, but slowly lets water pass.
When the contaiment is full, the water covers the pipes - but is still several feet from the transformer terminals.
I think the real issue is that a roof scupper drains into this area - where there are (2) 3000 kVA xfmrs, and (2) 2 MW gensets, flooding the area for the duration of a big storm.
I don't think the electrical system is designed to be subjected to water levels that result in water percolation into the building.
But as a first line of defense, we need to stop the flow.
I will likely recommed "sealing with an approved, listed material".
But if anyone can suggest a product I'd appreciate it.
Thanks
JM