Re: Wattage for 15A light legs
Originally posted by gudguyham:
Usually 80% of the available total is acceptable. So your figures of 1000 to 1200 is quite conservative.
Actually 100% loading is fine unless you believe that 100% of the load will be continuous.
I am also curious why Angus
(AC-DC) chose 117 volts.
220.2 requires the use of 120 as the voltage for computations.
A 15 amp 120 volt circuit can be loaded to 1800 watts.
A 20 amp 120 volt circuit can be loaded to 2400 watts.
Unless that full load will run 3 hours or more.
Continuous Load. A load where the maximum current is expected to continue for 3 hours or more.
What that means IMO is that some of the load can stay on forever as long as some of the load stops at least once every 3 hours.
If you decide your load is continuous then
A 15 amp 120 volt circuit can be loaded to 1440 watts.
A 20 amp 120 volt circuit can be loaded to 1920 watts.
Now that is code and code is a minimum standard for safety.
Most of the commercial jobs I work lighting circuits are 20 amp circuits and only loaded to 8 to 12 amps, that leaves room for changes and assures the breakers in the panels are running cool.
Meeting code and providing a good design are not one in the same.
[ October 08, 2005, 07:26 AM: Message edited by: iwire ]